Originally posted by bigrockk:
Well I have to put my two cents in.
If the stove is used as intended supper will be nice and hot. One has to remember that it is extremely unlikely that all elements will be on high at the same time. As such the load from each element will be cyclic, so highly improbable that the stove will ever draw 12KW even if the whole family is home for dinner.
Aspencade: In your first post you ask: That seems to mean that for calculations of service the conductors or breaker do not have to be de-rated to 80%. Does this apply to branch circuits as well?
No this does not apply to branch circuits. Rule 8-200 applies to Services and feeders only, not branch circuits. Rule 8-104(3) applies to branch circuits, and in my experience this means it is considered "a continuous load" unless you want to take the time to prove to the Safety codes officer (Inspector) that it is not continuous. There are exceptions but they are stated quite clearly in Section 8, such as 8-300.
It would be rare to find residential hardware (service box, fusible switch, circuit breakers or panel boards) marked for continuous operation at 100%. So in most residential cases rule 8-104(5) will apply.
Just my two cents....